Tractor Talk Discussion Forum
220 wire size Hello buickanddeere and T-Bone
john in la
07-28-2005 10:25:57
I really know better than to ask a electrical question here because of the answers you get BUT..... ..
Can some one tell me per the national electrical code what size wire you need for 220 at a set amps for a distance of 40 ft.
I need to run 3 220 lines for my new a/c unit.
Outside unit needs 40 amps. Inside unit needs 1- 60 amp and 1- 30 amp.
I am thinking I will need 30 amp 10/2 with ground
40 amp 8/2 with ground
and
60 amp 6/2 with ground
But would like to make sure before I go buy the wire.
dr.sportster
07-31-2005 09:59:44
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to john in la, 07-28-2005 10:25:57
The breakers in your picture also must have the HACR rating embossed into the plastic on the side of them.Otherwise they are not for HVAC use.
dr.sportster
08-03-2005 12:38:24
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to dr.sportster, 07-31-2005 09:59:44
Maybe all Square D breakers are already rated HACR,not sure[heating,air cond,refrigeration]
john in la
08-01-2005 13:04:29
Thanks for the info
dr.sportster
07-29-2005 11:53:39
Heres the info I got today.New labels on units will have two new specs:M.O.A [maximum operating ampacity] and MOCP[maximum overcurrent protection].Use MOA label to size wire as in 310.16 and 310.16 FPN[like number12 awg is for 16 amp max etc.]that gets you your wire size.MOCP label allows you to size the overcurrent protection or size breaker to allow for inrush current.Should be alot less wire and breaker sizing problems with these two new labels.So look for the MOA and MOCP spec on unit.
Dixieland
07-28-2005 14:07:25
Your thinking is correct assuming you use copper conductors and Type SE cable for the 40 & 60 amp circuits.
dr.sportster
07-28-2005 13:19:43
There are two new specs on the units to simplify what gets figured here.I did not take the seminar but my coworker did.I will find the initials[and meanings] of these specs and post tomorrow.AC unit labels have always caused some minor confusion for load amps apparently this is cleared up with the new two specs.
buickanddeere
07-28-2005 11:02:45
Don't worry. It's mostly questions such as the following that get the scathing remarks. Requests for info that is are clearly stated in the machine's manual(s). Lead additives for unleaded fuel, single weight Vs multi weight oils, oil change intervals and detergent vs. non detergent oils. I assume this AC system is setup 40ft from the building’s power distribution panel? There must be a resistive heating system built into the inside evaporator unit when it rated for 60.0 Amp? I wonder what the 30.0 amp is for? That's an awful large fan? Is this a water sourced heat pump or something? Most electrical codes and common sense requires a single isolation point be able to de-energize the whole AC system. Depending on which loads are motors and if they are centrifugal fans, scroll compressors or reciprocating compressors. The starting inrush current amount and duration of the inrush affects breaker and wire size. This maybe a situation where a common supply over to a main disconnect and local breaker panel right at the AC unit maybe required? Getting into wire this size I like to run it in conduit. It's certainly not any more expensive and it's well protected. Measuring a string pulled through the conduit then cutting the wire to length right off the venders rack reduces waste/$$$. Just depending, driving a ground rod(s) right at the outside AC unit maybe required or just a good idea. If trenching conduit into the ground, laying the bare #6 ground cable in the dirt works very well.
john in la
07-28-2005 14:18:18
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to buickanddeere, 07-28-2005 11:02:45
Thanks for the response. Lets see if I can give you a little more info.
This is a 3.5 ton heat pump.
The out side unit.
I have cinder blocks mortared together and the center filled with dirt. On top of this I have a 4" poured in place slab with the a/c unit set on this. I have it raised with the blocks to prevent mower from hitting unit and keeps it out of the dirt/grass level.
The unit is 220 and is marked min circuit amps 23 and max overload protection of 40 amps so I installed a single breaker box on the house next to the unit with a 40 amp breaker in it and a whip to the unit.
It is about 38 ft from the house 200 amp service entrance.
The inside unit is just on the other side of the wall from the outside unit. 4 or 5 ft at most separate the two units.
The inside unit is also a 220 unit and is marked min circuit amps 7.8/7.8 and max over current protection of 15/15.
BUT I have a 15kw backup elect. heater coil added to this inside unit for the really cold days since it is a heat pump. The heater coil is made to fit this unit. It came with 2 breakers pre wired to the heater coils. It also has a plug that you plug into the blower unit to provide elect. to the unit.
The wiring diagram for the heater coil says…….
Kilowatts 10.6/14.25
Volts; PH; HZ. 208/240/1/60
Heater Amps 50.96
The breakers are marked 10kA 120/240V
One of the breakers is marked 30 on the switch and the other is marked 60. This unit is also about 38 ft from the house 200 amp service entrance.
I think by the time I go around corners and into the units to hook up I will be at 45 to 50 ft max wire length.
I will be running the wire in conduit under the house to the inside unit closet area and then from here I will have the outside unit wire enter the back of the box through the wall and the inside unit wires enter the unit. I am waiting to see what size wire I need before buying conduit so I can get one big enough.
The link is to a picture of the inside unit breaker panel. If you click on the bottom right of picture it will explode to a size you can see all detail.
Thanks for the help.
John
Richard H.
07-28-2005 17:52:32
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to john in la, 07-28-2005 14:18:18
Hey John. Your wire sizes are correct. If you can run conduit all the way to each disconnect. One from the out side unit to the panel, ok to do because you HAVE to have a disconnect at the unit. Then you can combine the other two in the same raceway to there respective disconnects. The 60 amp circuit is for your back up heat. you should use THHN wire for all.
dr.sportster
07-29-2005 11:58:28
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to Richard H., 07-28-2005 17:52:32
You cant hard pipe to a unit.Seal tite or some type of flex must be used before the diconnect.I know what you meant but pipe does not go directly to any type unit.
john in la
07-29-2005 04:41:24
Thanks for the help Richard
I sent you a e-mail
If you did not get it let me know
John
Bus Driver
07-28-2005 15:30:45
Special rules apply to motors- Article 430 and AC units- Article 440 in the NEC. For your outside unit #10 will work and meet specifications AND could be used with a 40 amp breaker. Completely code compliant. #8 would add a slight bit of efficiency.
buickanddeere
07-28-2005 17:26:38
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to Bus Driver, 07-28-2005 15:30:45
Something doesn't jive. A 14.25 KW heater draws 60 amps when supplied with 240V, Not 50.96 amp. 50.86 amp and 240 V is 12.2KW. A 12.2KW heater, 7.8 amp fan and 50.96 amp figures with the 60 amp breaker but it's stretch. Usually a breaker isn't loaded past 80% for constant loads. If this heater is 12.2KW, a single 60 amp circuit breaker from your home service ran to a local disconnect at the compressor is absolute minimum. The 60amp inside breaker could be fed from the local disconnect at the compressor. Then power would be taken to the top of the 60 amp breaker to the top of the 30amp breaker for the compressor. That fan has to tie in there? Likely from the bottom of the 60 amp breaker to it's own relay & overload. The compressor and resistive heater won't be running together. A #6 and 60 amp or better a #4 and 80amp breaker from the home breaker panel. Along with a #6 bare ground in the conduit to the disconnect beside the outside compressor/condensor. Sorry but if your electrical inspector or insurance agent sees that 40amp setup. They will throw a fit. It will trip on the heater load. And two supplies to the same AC system from the same home breaker panel maybe frowned upon. A ground rod(s) driven at the compressor is a good idea and maybe required by code.
john in la
07-29-2005 04:12:35
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to buickanddeere, 07-28-2005 17:26:38
"Something doesn't jive."
I think you are looking at it wrong.
The fan (unit) is 7.8 min and 15 amps max. I take this to mean it is about a 10 amp fan. The heater coil is 50.96 amps so lets say 51 amps.
51 amps + 10 amps = 61 amps
To get breakers to be at 80% use you will need about 76.5 amps worth of breakers.
I have 90 amps. A 60 and a 30. Guess a 50 and a 30 would have worked but this is what they put in it.
The heater has 3 coils.
2 are run by the 60 amp braker and 1 is run by the 30 amp breaker.
The fan can be run by either breaker so that it will run in heat pump mode or heater mode.
In fact if you look at it this way you really need 90 amps to cover every situation because either breaker will run the fan.
90 amps x .80 = 72 amps
72 amps - 10 amps for fan on 1 breaker - 10 amps for fan on other breaker - 51 amps for the heater = only 1 amp over.
From what I have read and found out here I feel my wire choices will work.
buickanddeere
07-29-2005 09:24:54
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to john in la, 07-29-2005 04:12:35
Ok you are providing some info previously missing about the large and small bank of heaters. At 1st it appeared the heater was "one unit". The fan will run at about 7.8 amp. As 15amp breakers are the smallest common off the shelf breakers. Anything with running currents of less than 12.0amp are considered "protected" by the 15amp breaker. The fan supply could be tied in at the bottom of the 30 amp heater breaker but that's stretching the 30 amp breaker’s 80% loading rule. You have to have a local disconnecting means right at the compressor unit. It would have been cheaper and safer to run a single set of 80 amp breakers in the home service panel. And a single set of #4 copper to the top of the 60 & 30 amp heater breakers. Two sets paired breakers and four live conductors instead of two running over to the AC equipment. Would have been looked upon better by inspectors as well. They prefer to avoid multiple sources of power into a piece of equipment if possible. Where is the 40amp short circuit protection breaker, overload thermals and contactor for the AC compressor? Inside or outside? Where is the top of that 40amp breaker tied to? I wish I could see the whole setup in person and get an overall grasp of what the manufacture sent you. And I don’t intend to insult by saying what you have worked on and planned your best with, isn’t satisfactory.
john in la
07-29-2005 22:31:13
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to buickanddeere, 07-29-2005 09:24:54
Ok lets deal with the inside unit first. It is the one in the picture with the 60 and 30 amp breaker.
You are saying I should use a 80 amp breaker in the house 200 amp box and then run a 4/2 with ground wire from this breaker to the inside A/C.
How will I divide or hook up this 4/2 to supply power to the two breakers in the A/C???? (60 and 30)
I can under stand that having two breakers in the house box for the same A/C would be confusing. Turn only one off and thinking power is off you get a real jolt because you did not turn both off.
Next..... ..
The 40 amps is for the outside unit. I have a single 220 breaker box mounted on the outside of the house next to the compressor with a whip going to the unit.
There will be a matching 40 amp breaker in the house 200 amp box.
Thanks.
buickanddeere
07-30-2005 06:58:42
 Re: 220 wire size Hello buickanddeere and T-Bone in reply to john in la, 07-29-2005 22:31:13
If the breakers have large enough lugs. You can just daisy chain across from the top of one breaker to the next. Best bet would be to bring 80 amp #4 power to the disconnect beside the AC compressor. From the bottom of the disconnect into the 40 amp for the compressor. And also from the bottom of the disconnect to the inside 60Amp then daisy chain over to the 30amp. Good point there earlier about having to use flexable conduit into the compressor. I forgot to mention that. THHN wire is good stuff too. The #4 to the compressor 1st will assist starting when voltage is a bit low during utility brown-outs. Or if your service is loaded heavy with other loads. I do like to pound a 10' ground rod in for things like outside pool pumps, AC units etc.
T_Bone
07-28-2005 12:32:17
Hi John,
I'm with BD, more info on the inside unit or air handler as well as distance from load center.
The OS unit, 2-#8awg, 1-#10 neutral, and a #10??? bond ground wire if EPVC, no bond wire if EMT. The neutral will be needed for LV control circuits.
A fused disconnect with-in unit sight is also required. I seam to remember a no more than 6ft rule here for some reason.
A 2" thick concrete pad 4" larger than the condensor unit size is required for the unit to sit on. They use a different term for the concrete pad that I can't remember but most inspectors won't pass anything but concrete or concrete paving blocks layed tightly.
I'm unsure of the minimum bond wire size. Just been to long ago.
T_Bone